Wiring up Tado thermostat

Any idea how to wire up a from Drayton to Tado?
I have 1 Blue, 1 Red and 1 yellow cable from the Drayton.

Can someone tell me which ports I need to put them in on the Tado?

Many thanks

Best Answers

  • GrilledCheese2
    GrilledCheese2 ✭✭✭
    Answer ✓

    ASSUMING the Drayton is wired correctly. Blue is Neutral and should be connected to P1 as this wire is not used by Tado. The red wire is Live and should be connected to COM. The yellow wire is Switched Live and should be connected to NO.

    If there’s a loose Earth wire you can connect it to P2. The P terminals are just used for parking unused wires.

  • GrilledCheese2
    GrilledCheese2 ✭✭✭
    Answer ✓

    If you’re referring to wiring up a hot water controller, there’s too many permutations to guess the function of the yellow wire and where to put it.

Answers

  • That’s great thanks! I’ll give it a go!

    Also what port does the yellow cable go into for the hot water Tado?

    Many thanks
  • Thanks, all sorted now, fortunately I just had to swap the units over, the back plate was the same! Result!