In what steps can the radiator valve regulate heat? And for the thermostat?
Answers
-
So as a further update, I also asked Jurian if the wavy lines correspond to the valve position, or to heater demand. He’s saying this:
- Tado works with a PID controller (https://en.m.wikipedia.org/wiki/PID_controller)
- No waves correspond with < 5% PID
- 1 wave corresponds with 5%-33%
- 2 waves 34%-66%
- 3 waves 67%-100%
Personally, I don’t know a thing about PID, except for the Wikipedia article is just Googled. But... maybe one of you guys know more?
1 -
This seems to me to be consistent.
To put it simply, a pid controller, if properly tuned, does much better than an on/off controller. It drastically reduces overheating and underheating. I notice that as the days go by, the system adapts itself better and better to the heating demands.
0 -
Hi @Schippie,
There are percentages next to the wavy lines on the Care and Protect page. I assume that you are talking about the relationship between the wavy lines and these percentages. As far as I can make out these percentages represent demand rather than controller output. The demand signal is modified by PID functions to give the controller output which is what controls the valve.
Not much more than two weeks ago I put in a suggestion that Self Tuning PI Controllers (or indeed PID) should be used - combined with improved temperature measurement. This suggestion has already been moved to "The Big Idea Archive" That was a bit quick! Perhaps because they already have a form of PID control which they are happy with or perhaps I should have not been too specific regarding the suggested solution.
I assume and also it would be logical that the Tado PID controllers are on their servers - following the Tado goal of being Hardware Agnostic.
My archived suggestion was intended in particular to suggest that the controllers should be "Self Tuning". I would be interested to know if they are. A PID controller is not necessarily self tuning. If a controller is correctly tuned, any fluctuating +ve and -ve deviations of the measured value from the set point will noticeably diminish over a short period. You should be able to see this effect an a graph.
The bottom line is that it is not easy for the controllers to adapt to many different systems. For instance half of my system is microbore so some of my controls would be in saturation for lengthy periods (i.e. controller output at 0 or 100%).
Finally, proper control is impossible without reliable and accurate temperature measurement and vertically mounted SRT's (with built in temperature sensors) fitted close to the radiator definitely do not give that.
0 -
Hi @Schippie,
There are percentages next to the wavy lines on the Care and Protect page. I assume that you are talking about the relationship between the wavy lines and these percentages. As far as I can make out these percentages represent demand rather than controller output. If the percentages are controller outputs there must be some other limit on how often the valve actuators can move as they do not move every time the percentages change.
Not much more than two weeks ago I put in a suggestion that Self Tuning PI Controllers (or STPID) should be used - combined with improved temperature measurement. This suggestion has already been moved to "The Big Idea Archive" That was a bit quick! Perhaps because they already have a form of PID control that they are happy with or perhaps I should have not been too specific regarding the suggested solution.
I assume and also it would be logical that the Tado PID controllers are on their servers - following the Tado goal of being Hardware Agnostic.
My archived suggestion was intended in particular to suggest that the controllers should be "Self Tuning". I would be interested to know if they are. A PID controller is not necessarily self tuning. If a controller is correctly tuned, any fluctuating +ve and -ve deviations of the measured value from the set point will noticeably diminish over a short period. You should be able to see this effect on a graph.
From what I can see, there is some room for improvement in both temp measurement and control.
The bottom line is that it is not easy for the controllers to adapt to many different systems. For instance half of my system is microbore so some of my controls (compared with in other rooms) would be in saturation for lengthy periods (i.e. controller output at 0 or 100%).
Finally, proper control is impossible without reliable and accurate temperature measurement and vertically mounted SRT's (with built in temperature sensors) fitted close to the radiator definitely do not give that.
0 -
However many steps the TADO TRVs are capable of opening and closing in I can tell you they are far more effective than some of their rivals. As a recent TADO convert its a pleasure to hear the valves open, and feel the radiators beginning to warm, moments after a call for heat rather than the ~ 20 minutes previously tolerated . . .
3 -
So I asked some additional questions to Jurian (who's really quick to respond, by the way) concerning the relationship between tado modulating the radiator valves and modulating the heating request from the heater. He told me both operate in around 5% steps, and are related but not necessarily the same.
He did mention that when only 1 tado valve requests power, it will always open 100% and modulate the required heat only. When 2 or more valves request power, both will modulate.
Maybe that explains the somehow contradictory explanations so far. So valves will open/close only when 1 valve requests heat. If more do so, both valves and heating request will modulate apparently.
1 -
Hi @Schippie,
We learn a little step by step...
My reference to "demand" was actually meant to refer to the error signal or PID controller input rather than to the PID controller output signal. Despite all the various posts and speculations on the subject I am still no wiser as to precisely what the percentages on "Care & Protect" actually represent.
Due to the fact that Tado users are on multiple different configurations (relay, Opentherm, combi, heat only etc) we are not always comparing like with like if we get too specific. My system is a relay heat only Y plan system with vented hot water tank and Tado extension kit. If Opentherm is an option for me I might consider it, but am probably more likely to go for the weather compensation system that is available for my boiler (a Viessmann) as I can then have some influence on which weather compensation control ramp is in use.
For me even with only one SRT in use it seems that it can be partially open and I need to have another radiator online with no SRT to ensure that the boiler is not locked out by low flow. Perhaps that is what applies to my particular set up...
0 -
Hey @Schippie
Your response from @jurian reminds me of an old "Morecombe & Wise" sketch with Andre Previn......when Eric replies to A.P.
" I'm playing all the right notes but not necessarily in the right order " 😎 🤣1 -
Sorry @GrayDav4276 that reference flew straight over my head 😉0
-
Ahh.... You youngsters.....🤓 It's a comedy classic....I'm sure it'll be on YouTube 👍0
-
Anyway, I am certainly no expert on heating. But I have now upgraded all my radiators so they are capable of control by thermostatic valves, I put tado srv’s on them, and with the new bridge tado sent me... all rooms are now connected without issue. As the upgraded radiators allow for setting the max heat flow, I also got rid of the temperature spikes. Have to admit it, things seem to work ok now. Only need to add a zone valve for the floor heating, and things are set.
I still strongly feel tado should improve user control over the heating strategy and fix early start.0 -
I read this thread with interest as one of my radiators is constantly overshooting by 2 or 3 degrees. It is the radiator in the kitchen, which is almost next to the heater. Before I had Tado that radiator would be open about 25% all the time to prevent it from heating too much and returning too hot water back to the heater. I suspect it's now opened too much before it overshoots.
Is there a way to limit the opening of a Tado valve to combat this?
@Schippie you mention you limit the max flow. That sounds like something that could help me. How do you do that?
0 -
@hapklaar I don't know a way to limit opening of the Tado valve, but you can certainly adjust the lockshield valve at other end of the radiator to limit the water flow through the radiator. This should have the same effect.0
-
I have found some information about your question you might be interested https://shrinke.me/8GzQA38h
-2 -
[Quote]"He did mention that when only 1 tado valve requests power, it will always open 100% and modulate the required heat only. When 2 or more valves request power, both will modulate."[/Quote]
In my recent experience this is, unfortunately, absolutely untrue. I've had a single radiator calling for heat at 23% (whatever that means exactly), boiler on, and zero flow through the radiator. The valve simply was not open enough to allow water to pass. I do have a bypass rad, so that gets 95% of the heat while the room that actually wants heating gets almost none, or actually none.
Indeed I am extremely suspicious that battery preservation had taken precedence over optional functioning of the heating. Far too often I see only one or two radiators calling for heat, but with only modest valve openings. Well my boiler cannot output less than 9kW, so with only one or two radiators sipping water instead of glugging it down the boiler shuts off prematurely as target flow temperature (set by ebus) is reached before the radiators have even seen any of it. I've seen burn times as short as 30 seconds on occasion, followed by the inevitable five minute pump overrun as a thimble full of tepid water is pointlessly circulated round the system. How is that a sensible way to run a system?
If the radiators are balanced it is even worse, with radiators choked off at both ends. There is no point that I can see in having partial valve openings in these (or any other) circumstances. If the radiator needs heat then have at it. The boiler will thank you.
0 -
@eezytiger Interesting. Is there any point having the radiators balanced if they all have a Tado TRV fitted, or would it be better to have the lock valves fully open?0
-
@johnbur I do have my suspicions that, with valves as responsive as those controlled by Tado, the benefits of balancing are questionable. For the most part it is generally the case (in my house) that only a few radiators request heat at any one time. This rest are actually shut off and not bleeding off heat, leaving plenty for those that need it.
Also, my heating is on 24x7, since the house is usually occupied. Therefore the heating doesn't have to play catch up, as it might in the evening for a house unoccupied during the day. So when heat is needed in a room it will not take long before it is up to temperature, so once again heat is available to other radiators soon enough.
With this in mind, although I did go to the trouble of balancing my system, I have actually backed off some of the lockshield valves following observation of operation of Tado. That said, I do believe that Tado has improved on the partial opening performance of the valves, reducing this silly trickle nonsense, so I think it is possible to be more relaxed about the lockshield. But I would say better a little more open than a little more closed.
0 -
@eezytiger thanks - that reassures me - I'd come to the same conclusion a couple of years ago - opening up the lock shield valves on the further away balanced rads made a big difference - we're in the same situation that a lot of the time only one or two rooms are heating, so they get to temperature a lot quicker now.0