w.Intercom = i;img.ProfilePhoto.ProfilePhotoMedium { padding: 10px; }Set a Minimum Central Heating Flow Temperature (OpenTherm) — tado° Community

Set a Minimum Central Heating Flow Temperature (OpenTherm)

Hi,

The main purpose of this post is to try and gain an understanding of whether setting a minimum central heating flow temperature is a feature that other users of this forum would value and like to be developed by Tado as part of their algorithms. Are there any other users out there that have abandoned using the OpenTherm protocol due to low demand boiler start up cycling? 

For me, I would like to be able to define a minimum flow temperature in the same way that we can set a maximum flow temperature within the professionals Tado app although I’m also open to the idea of demand curves.

A couple of weeks ago - I installed a Tado v3+ smart thermostat in my home using the OpenTherm protocol but unfortunately, it appears that my boiler is often left repeatedly cycling the ignition sequence with three minutes of pump overrun. This happens at times of low demand usually in the evening when the house is already up to temperature – Tado appears to be requesting a 25c central heating flow temperature for 0.2c top ups.  

At the moment I am manually intervening to stop the cycling by increasing the thermostat temperature from 20.5c to 23c in 20 minute blocks. At 23c, Tado increases the flow temperature setpoint to above 32c. Above this setpoint [32c+], the boiler seems to run quite well.

For the remainder of winter, I will change the setup from OpenTherm to Relay (+ outside weather compensation) but ideally, I would prefer to continue with the OpenTherm configuration if I can set a minimum flow temperature to stop the cycling.  

I would be grateful if other users who would like to see this feature developed could comment below as it’s not currently something that’s on Tado’s development radar and I’m unsure if it’s just me that’s been affected by this when trying the OpenTherm configuration.

PS my case is already logged with Tado support as they have made alterations to my PID but unfortunately to no success with the cycling issue.  

15
15 votes

Active · Last Updated

Welcome!

It looks like you're new here. Sign in or register to get started.

Comments

  • Valaki1234
    edited October 2023
    Usually you can configure both the minimum and maximum flow temperatures in your boiler.

    About the cycling: for long time I thought my boiler cycles because too low flow temp is requested, then I realized it was caused by the SRTs. Too many were closed at the same time and for heating e.g 1 single room the boiler needed to cycle as the flow and return temps were really close. So I removed all SRTs and the boiler cycles significantly less.
  • _C_
    _C_
    edited October 2023

    When configured for OpenTherm all of the controls on my boiler are disabled as it becomes a slave.

    All of the TRVs are open to max and the system is balanced - I prefer to heat the whole house rather than individual rooms. The towel rails and hallway don't have TRVs.

  • On my Baxi boiler I can confirm that those settings are not overwritten, I also use OT.
    Having MIN setting only makes sense if the boiler uses it so it it would be strange if it is overwritten when connected via OT as in simple relay mode it is useless (maybe in there are other digital connection methods ?).

    Good strategy what you follow, I also do the same. Why do you assume that the root cause of the cycling is Tado asking for too low temperature ? Do you capture OT communication ?
  • _C_
    _C_
    edited October 2023

    Which model of Baxi boiler do you have? I have the Potterton Promax Ultra 40 which is technically a Baxi.

    Like most boilers, I can set a flow temperature using the +/- buttons below the display when it is in relay configuration and the IFOS is disconnected. There doesn’t appear to be an option to define a min central heating flow temperature.

    I can see the central heating flow setpoint on the information display after pressing the information button until it reaches information point number 9.   It’s useful as I’ve not had to place a gateway between the boiler and Tado. It’s also useful to watch Tado decide on what setpoint to use before the boiler fires up.

    edited (added below):

    It’s exactly the same type of issue if you deliberately select a really low curve on warm day when the IFOS weather compensation sensor is plugged in.

  • Valaki1234
    edited October 2023
    I have a Baxi Luna Duo-Tec E bought in 2022.

    Using the plus-minus on the panel only set the temperature to be used in relay mode.
    For OT you need to turn on the ‘advanced’ menu which will enable many additional parameters.

    In my case I needed to enter into the parameter settings menu then navigate to parameter 22 and set its value to 22. This enabled many additional parameters, the ones I use:
    - 16: to set the MAX temperature used in OT mode. Not the same what you can set via the +/- buttons on the main panel
    - 67: set to 2 to use OT standard protocol
    - 83: to set the MIN temperature used in OT mode
  • I’ll have a look for the advanced menu and parameters.  I know that a minimum central heating output can be defined as a percentage but that’s not what I’m looking for.  I’ve never seen a parameter for a minimum flow temperature like there is for a maximum reachable flow temperature but I’ve never actually looked for it until now.

    I think my main objective of this thread is to help make OpenTherm low voltage controls more accessible to people who happen to have high powered combi boilers that struggle to maintain flow temperatures as low as 25c - whether that’s during the ignition start up sequence and / or due to the modulation ratio that their boiler offers.  

    I didn’t choose the boiler that I happen to have, it was spec’d by a large UK housebuilder and most likely based on its ability to deliver instantaneous hot water.

  • Hi, just letting you know that I found your post while searching for the exact same thing for my NEST stat! I used to have Tado at my previous property connected to a Baxi 600. I'm not sure if it was because that home was not so well insulated or what but I never noticed a short cycling issue there. In my new home where I've just had an Ideal Logic Max Heat 2 fitted with NEST I am experiencing the short cycling and have come to the same conclusion that there needs to be an option to set a minimum flow temperature request. Great minds.

  • _C_
    _C_
    edited December 2023

    Yes, Tado should implement this.

    I was able to resolve my cycling issues in the end by setting a minimum central heating flow temperature of 45c with help from Valaki1234 who convinced me that there is a minimum central heating setting (P83) – I think our boilers have similar controls.  I also used Google to translate the advanced Baxi manuals from the Czech Republic (I’m English / UK based).

    Opentherm is working perfectly now and the boiler is not on all day like some people describe their Opentherm experience – it heats the house up in the morning at 60c (my Max setpoint) if the house setback drops over 1c through the night then for the rest of the day it comes on now and again at 45c for top ups.

    If Tado are reading this then I think they should have a look at what Home Page - EPH Controls are doing with their Opentherm products as they appear to have a minimum central heating setpoint (see pic below).

    EPH.png

    I’m really happy with how the boiler, Tado and Opentherm are working together now. 

    My settings changes to my boiler currently are :

    Range rated DHW and CH to suit my property

    P18 - Delay prior to new ignition in CH mode = 10mins (was 3mins)

    P22 change to 22 to display advanced menu:

    P83 - Minimum boiler temperature in heating mode = 45c (was 25c)

  • C3ham
    edited January 2024
    I have the exact same issue when tado requests low flow temps my boiler can’t modulate low enough(6.8kw is the lowest it goes) so cycles every few minutes would be amazing if tado could add a low flow temp setting and all my tvrs are set to max so it’s not because rads are shutting down
  • @_C_ would you be able you provide by any chance details or the manual how you managed to configure configured this on the boiler (aka how to get to advanced menu)? As it happens I have exactly the same boiler and I'm thinking of installing the opentherm with it

  • Hi @sycyhy

    If you hold both of the radiator buttons - / + in for 6 seconds the display should show P01. The display might flash P01 and the currently assigned value for it.

    Press the + radiator button to start working your way up through the advanced menu options i.e. P01, P02, P03 etc. When you get to the P number that you want to change, press the i/P button.

    You can then use the - / + radiator buttons to change the setting value for the P number. After you’ve changed the setting, press the i/P button to lock the setting in for that particular P number. You can then carry on pressing the + radiator button to move onto the next P number that you want to change the setting for.

    I’ve made the following changes on my Potterton:

    These first two are specific changes to the way I want the boiler to operate in my new build property - Range rated Central Heating and DHW Output:

    P13 Max. heating output (0-77%) - 27%

    P14 Max DHW output (0-100%) – 75%

    P18 - Delay prior to new ignition in CH mode = 10mins (was 3mins)

    P22 change to 22 to display advanced menu. You can only see P83 when you change P22 to 22 and you have to do this every time you want to change P83. It’s like the P numbers after P42 are hidden.

    P83 - Minimum boiler temperature in heating mode = 45c (was 25c)

    Half way up through the P numbers you might encounter some CO numbers – I think these are a log of previous fault codes. Just keep pressing the + radiator button to move back onto the rest of the P numbers.

    I've included a picture below of the non advanced menu options - number 9 shows the set point that Tado has sent through to the boiler. That's how I knew my Tado was requesting a 25c flow temp which is far too low for my boiler to even make it past the ignition sequence.

    menu.jpg
  • Thanks - really appreciate that! super helpful

  • @_C_ on a very similar topic. I found the czech pdf that you were mentioning before, and there is few other interesting options. As an example - I have the 40kW version as well, it is a bit too powerful for my house so it's a bit of waste. Seems there is a setting (P73) that you can basically make it 32kW if you need.

    If I understand correctly your settings, this is something very similar what you were going for with P13, P14 - or this is something completely else?

  • P73 looks like the power settings specific to the different products that the circuit board is also used in. I'm leaving that setting as is. My heating only needs about 12-15kw and on demand hot water needs about 30kw as the taps and showers have flow restrictors.

  • Sorry for resurrecting an older thread.

    I have the Potterton Proxmax Ultra 40 combi (oversized for my seven year old 2 bed semi) and I'm attempting to make similar optimisations of a low flow temp without the constant flame on/off.

    I've accessed the Advanced Parameter menu (pressing rad keys + -), however, even with P22 set to 22, the maximum menu I can reach is P76 on my boiler - no P83.

    I can't seem to find the Czech pdf mentioned above - does anyone have a link, please?

    Alternatively, which Baxi boiler is mine equivalent to?

    My room stat is a Honeywell CM907, soon to be replaced by the V3 or X stat - still researching.

    Many thanks

  • My Potterton boiler is a 2018 (year) model and it looks a little bit like a Baxi Luna Duo-tec

    I would have abandoned Opentherm if I was unable to set the minimum flow temp (using p83) as I was unhappy with the way it was running when Tado sets the setpoint at 25c.

    Here is a Google search URL that should bring back the Czech service manual:

    https://www.google.co.uk/search?q=SERVISN%C3%8D+P%C5%98%C3%8DRU%C4%8CKA+baxi

  • @_C_  I just wanted to say a big thank you for the hard work on this. I stumbled on the thread a couple of days ago and have been reading around this all as much as possible, on here a Home Assistant thread regarding converting a boiler to OT.

    Like you, I have the Potterton Promax Ultra 40, also from 2018 in a new build in the UK (Kent area actually). The developers zoned my house with Myson Power Extra motorised valves to separate upstairs and downstairs heating. I had Nest gen 3 thermostats installed to replace the rubbish that the builders put in as I wanted a smart thermostat - heat links are directly connected to the valves and the valves call for heat when opened (at least thats how it all looks when I trace wiring). Around the time of moving in and getting the Nest thermostats fitted I had heard of OpenTherm and over the last few years it came up time and again however I thought the boiler wasnt OpenTherm compatible. Then a couple of weeks ago I had a quick read through the installers manual just before getting a plumber in to do a service and I noticed that M2 will allow an OT thermostat to control the boiler. Bingo! Back to searching through OpenTherm information.

    The problem I have is having 2 zones, Nest thermostat doesnt support zones with OT and I didnt want to change out both my themostats for something like EPH or a different OT capable zoned system. So I started looking into making the heating back to 1 zone without having to get a plumber involved to rework pipes - I have settled on setting both zone valves to manual override and having them permanently open. 

    Another reason to go with the manual override back to one zone on the valves is because the house is a new build, the radiators have been underspeccd (well, speccd correctly for the house but not correctly with the minimum the boiler can output) - in total I have 7.1kW of heat output from all radiators ( 3.3kW downstairs and 3.8kW upstairs). If I intend to run the boiler at a low return flow temp by modulating with OT then I need all radiators as 1 system, not just an upstairs zone and downstairs zone as I wouldnt be able to loose heat fast enough into the house and the boiler would start cycling potentially. I learnt all of this on the Home Assistant community pages (here if anyone is interested https://community.home-assistant.io/t/opentherm-gateway-thermostat-with-full-integration-for-home-assistant/617228/205?u=townsmcp ) because I was looking to try to link both Nest's together via some sort of OT Gateway which doesnt seem to be a vailable option.

    As a proof of concept, I have turned the boiler heating temperature down to 57c (still in on/off mode so just used the panel control to change the boiler heating temp down) - I am already seeing more condensing mode operation as the return flow temp is around 46c. I have also set the upstairs valve to manual override - when downstairs now calls for heat upstairs heats up as well and the manual override isnt calling for heat constantly. I have even gone on to create automations in Home Assistant so that if someone changes the upstairs thermostat temp, downstairs will also change so that both zones heat up - again so that I get the condensing mode operation of the boiler rather than return flow temp being pretty much only a couple of degrees less than the boiler heating temp.

    In the next couple of days I will be rewiring the downstairs nest Heat Link OT connections to the boilers OT connections and the info you have provided above is invaluable for setting that minimum flow temp (as Nest cant handle it properly either from what I have read), just a shame the boiler manual (English version) doesnt have all this extra information

  • Hi, glad you found the information above useful - my house is a newish build and I was expecting to have two zones as the same house type on the neighbouring development had two zones. Luckily with my build they created just one zone.

    I’m thinking about moving the downstairs living room radiators into the bedrooms upstairs and then buying two double panel radiators for the living room to create a larger system. I would like the boiler to run for longer periods but dissipating 6.2kw at a 45c flow temperature is going to require bigger radiators.

    I would like to replace the Potterton and (Opentherm) Tado with a Viessmann 200-W but from what I’ve read the Potterton seems quite a robust design so there’s probably a few more years left in it yet.

  • Townsmcp
    Townsmcp
    edited February 21

    The only type 22 radiators in my house are the one in the lounge and one in the kitchen/diner. All others are type 11.

    To get flow temp down, might be worth a look at the setting sycyhy mentioned above?

    I did notice the manual for Baxi-Duo-tec-E-Manual does also show how to set parameters in English on page 14 of the PDF (the Czech manual cover does say it applies to that boiler also). I found the manual on Central Heating NZ website (https://www.centralheating.co.nz/assets/resources/Baxi-Duo-tec-E-Manual.pdf) - I havent cross checked yet though that the information is the same between Czech and NZ manuals.

    Ignore this - I just checked. The P codes do not go above P67. It all references to check the Service Instructions. Found the English version of the service instructions at https://service.baxi.ru/info/download-other?name=%D0%A1%D0%B5%D1%80%D0%B2%D0%B8%D1%81%D0%BD%D0%B0%D1%8F+%D0%B8%D0%BD%D1%81%D1%82%D1%80%D1%83%D0%BA%D1%86%D0%B8%D1%8F+%D0%B4%D0%BB%D1%8F+%D0%BA%D0%BE%D1%82%D0%BB%D0%BE%D0%B2+DUO+TEC+%28ENG_%D0%BD%D0%BE%D0%B2%D0%B0%D1%8F+%D0%B2%D0%B5%D1%80%D1%81%D0%B8%D1%8F%29.pdf

    Quick question - does the Tado have local weather compensation that it passes over to the boiler via OT? Reason I ask, is in the Potterton manual, page 53 of the PDF, section 18.1.3 alludes to setting the outdoor sensor curve before connecting the OT device. I was wondering, if the OT themostat does pass over weather compensation data, does an outdoor curve need to be set (personally I dont have the Potterton outdoor sensor so Im not sure if this section only applies to Potterton outdoor sensor & OT thermostat)?

  • _C_
    _C_
    edited February 21

    Hi, I have the IFOS outdoor sensor but it’s currently unplugged as the Technical Agent at BAXI told me that it is best to disconnect it when using an Opentherm control. ‘disconnect the IFOS as they can interfere with each other’ is what they said.

    Another reason is that some of the controls become locked out once Opentherm is setup.

    Tado without a subscription adapts how often the heating is on based on how sunny it is – I don’t think it adjusts the flow temperature with the free version. It’s a feature that all users can benefit from.

    If you have the paid subscription and Opentherm you can use their recently introduced flow temperature optimisation feature which is influenced by the outdoor temperature. I’ve not tried it this winter – I might try it next winter, however, I don’t see how Tado can make this feature appealing to a user like me that has had to apply a mininum flow temperature override (the purpose of this thread).

    For example - If Tado (without a subscription) requests a flow setpoint of 25c but with flow optimisation it would have requested 30c because it’s cold outside I’m still not going to benefit from it because I’ve had to program my boiler to provide a min flow of 45c until Opentherm requests 46c or above (only at this point will my boiler will accept the setpoint via Opentherm).

  • So I managed to do the conversion today. I popped some Wago connectors on the Call for Heat and Common cables on both Nest heat links, wired up a new cable from the boiler OT ports to the heat link port on the new master thermostat and powered everything up - so far, it seems to be working. One question for you though @_C_ have you found a menu on the Information (push and hold I button) that will show you the amount of gas being used to confirm that the boiler isnt just pushing through full on/off gas usage - effectively to prove that it is modulating the gas usage and therefore that OT is working as expected? I havent set the minimum return temp yet as I thought I would see if the boiler starts cycling before going down that rabbit hole

    I do wonder if the service port on the front panel of the boiler will allow an OpenTherm Gateway be connected permanently to be able to see and intercept the OT messages

  • These boilers modulate the output regardless of whether the connection is Opentherm or Relay (on/off). The only thing that changes with Opentherm is the flow temp set point. You could look at the fan speed (info item 17) but I've got to the stage where I know exactly what it's doing by the sounds that it's making.

Welcome!

It looks like you're new here. Sign in or register to get started.