Does the increased boiler firing/stop cycles prematurely age the boiler?

Hi,

Does the increased boiler firing/stop cycles prematurely age the boiler?

I believe that a boiler, and it's constituent parts, have an MTBF that cumulatively set an MTBF for the boiler in terms of number of firing cycles (affected by lots of other factors, to be sure) but nevertheless, doesn't the TADO controller increasing the number of firing cycles 5 fold equate to reducing the MTBF of the boiler by 80%?

And if the boiler is an older mode, and is more fragile, increase the chance of failure sooner rather than later?

Best Answers

  • eezytiger
    eezytiger ✭✭✭
    edited December 2022 Answer ✓

    My boiler has a minimum output of 9 kW and my heating needs today, since midnight, are just a little over 2 kW. Therefore my boiler only needs to be on for about 15 minutes per hour on average (today at least). So far, as we near midday, the boiler has fired 14 times. It may be 15 times by the time midday arrives.

    Given the constraints forced by the boiler's excessive output I do not know how the cycling could be reduced further. I don't think Tado can be blamed for an oversized boiler.

    Here you can see the firing pattern since midnight for the master bedroom, which is the only SRT linked to the zone controller. Temperature settings have been fixed throughout the time period - no scheduled temperature adjustments. 19C target for the past 24 hours and counting.

    The only way to improve matters would be to have a boiler more suitably sized to the needs of the property. Even with temperatures below zero for days on end the cycling was unavoidable. At worst case (-5C) the house didn't need more than 5 kW. Stupid boiler - well, stupid choice of boiler. But when it was fitted eleven years ago I did not know what I know today. Nor did I have the insulation that I have today.

    With all that said, it is worth noting that Tado used to fire the boiler for as little as under four minutes per cycle (3:40 with my boiler characteristics) but, as I've range rated my boiler to 9 kW, each firing cycle wasn't doing a lot, so I requested the minimum burn time to be raised to ten minutes. That does mean longer burns less frequently, so less cycling. If people are running Tado on out of the box defaults, with every SRT talking to the zone controller and able to demand heat, it could be a very different picture.

  • eezytiger
    eezytiger ✭✭✭
    Answer ✓
    @StavrosK Yes, the ten minus minimum firing is arranged through support.

    As for other tweaks, I haven't asked for any, but there is a known problem experienced by some, including me, where an SRT may be requesting heat and is firing the boiler, but the valve has not opened sufficiently to allow any flow to pass. I've dealt with this in my own way with the way I've set up temperature targets and independent rooms so that it is no longer a problem. For others I believe you can also put in a support call to ask for increased opening for such valves.

Answers

  • I think you’d struggle to gather any facts to sustain this suggestion.

  • wateroakley
    wateroakley Volunteer Moderator

    In practice, most age/use related failures I’ve come across are the zone valves.

    Reasons? 1. Age. 2. Brother in-law fiddling. 3. Boilers do fail and (for the boiler electronics) the mtbf of electrolytic capacitors halve for every 7 deg C temperature rise. 4. Can’t think of anything particular that I’d put down to a boiler firing cycle.

  • @StavrosK yes, it will, but should not materially adversely affect boiler lifespan.

    I’ve had to replace ignition electrode on my Viessmann, probably due due to firing rate, but the boiler’s been running with Tado for 10 years and been in for 13.

    All modern stats use TPI these days, if relayed. If they’re modulating instead/as well (if WC fitted, for example) then they’ll likely cycle even if relay isn’t switching them on/off due to poor modulation ratio and low flow temp.

    In a nutshell, yes, but shouldn’t be an issue.

  • @wateroakley @DM932187 I thought it likely. Just 3 weeks after I started using the boiler this winter, with the updated Tado App, the fan on the boiler seized up. The boiler is quite old, but has been serviced regularly. It might be coincidental, but I would rather have the boiler fail in 3 months rather than 3 weeks :-(

    Is there any way of reverting back to the older way of boiler usage - call for heat, stay on until target temp is reached, then switch off, rather than call for heat, on, off, on off etc until either target temp reached or, if a manual call using a timer, time runs out?

  • Hi @eezytiger ,

    Thanks for the info in your post, my boiler is most probably over sized also, but I can't change that now :-)

    You say you "requested the minimum burn time to be raised to ten minutes" - how? is that via Tado Support or can it be done via the app or online somehow?

    Any info on other tweaks that are available for the Tado defaults that might be useful?

  • Thanks @eezytiger that is very helpful. 🙂

    Happy New Year !

  • Irek85
    Irek85
    edited December 16
    @eezytiger I'm in the same boat with oversized boiler. I have a question regarding your heating time being set to 10 minutes minimum? Doesn't it cause your boiler to shut down due to getting too hot? If one small radiator calls for heat, how can oversized boiler be kept heating for 10 minutes? I guess I miss something, please educate me 🙂
  • eezytiger
    eezytiger ✭✭✭
    edited December 16
    @Irek85 I've got various mechanisms in play to avoid that....

    1. I have range rated my boiler down to the minimum output of 9 kW.

    2. I have multiple bypass radiators, so there is never only one radiator emitting heat. The hall radiator is with the smart wired thermostat, so it is always the primary bypass. Landing and kitchen radiators are undersized so the Tado SRTs are loose fitted and cannot close the valves.

    3. Only the lounge SRT is permitted to call for heat. All other SRTs are independent and must wait for the lounge to make the boiler fire. Thus, when the boiler does turn on, most radiators are open and ready for heat one way or another. The lounge radiator is actually also fitted loosely, so it can never be in the stupid position of calling for heat with the valve still closed.

    4. We are a retired couple. Heating is set to 16C overnight, 20C daytime. Therefore there is only one ramp up of heat per day, which can trip the flow temperature cutoff once water reaches 53C. After that the heat requirements are just maintenance top ups, periodically, so the flow never again reaches the set max throughout the day.

    5. We do not micro-zone the house. All rooms are set to 20C, except the lounge, which dictates the heating schedule between 16C and 20C. No rooms are turned off. We heat the whole house as one. It's basically applying heat pump operational style to our combi boiler. Low and slow heating throughout the property instead of lots of individual heating sprints everywhere.

    I've come to this arrangement through trial and error over three years of Tado ownership. I do experiment from time to time with alternative arrangements, but this is my setup right now.
  • eezytiger
    eezytiger ✭✭✭
    edited December 16

    p.s. flow and return temperature graphs for yesterday attached….

    Something I forgot to mention above, which is my latest experiment, is to only raise target temp by 1C per hour in the morning instead of leaping from 16-20 in one go. This also helps keep flow/return temps lower than going full blast for a couple of hours. You will see that reflected in the ramping temperatures from 07:00 onwards rather than the boiler bouncing off the 53C "rev limiter" repeatedly.

  • @eezytiger
    Thanks for your explanations and sharing detailed rules you use. Did those changes affect your gas consumption or boiler behaviour mostly?
    I love your temperature flow charts - how do you get them? Does your boiler app provides those?
  • eezytiger
    eezytiger ✭✭✭
    edited December 17
    I have two Bluetooth temperature logging thermometers fitted to flow and return pipes from the boiler.

    https://www.amazon.co.uk/gp/aw/d/B07DRC4M88?psc=1&ref=ppx_pop_mob_b_asin_title

    Yes, my refinements seem to improve flow/return temps and my general trend in gas consumption has been downward since fitting Tado (and new glazing and doors), but also since coming to understand so much more about boiler efficiency and things that can be done to improve it.

    Unfortunately, weather variations and other things make like for like comparisons difficult from year to year, but this year will see my lowest total gas consumption in the past six years, even though we've raised room temps a bit this winter.

    2018 11,536 kWh
    2019 11,294
    2020 10,762
    2021 13,102 New glazing in July. Tado installed in October
    2022 8,242
    2023 8,898
    2024 7,402 to date. 8,102 full year estimate
  • @eezytiger I'll try to get something similar, thanks! Hopefully I'll get similar savings as you!🙂