Boiler constantly on not turning off when temp reached
Hello,
I have just set my Tado v3+ wireless system up to my baxi 105 he boiler and the problem I have is the central heating is constantly on.
I have capped the old thermostat as to the instructions and wired the receiver to the boiler as to the instructions. So currently I am running off my old timer system.
If I ask the Tado to heat the receiver clicks to turn central heating on but the boiler doesn’t respond.
Any help would be much appreciated
I have just set my Tado v3+ wireless system up to my baxi 105 he boiler and the problem I have is the central heating is constantly on.
I have capped the old thermostat as to the instructions and wired the receiver to the boiler as to the instructions. So currently I am running off my old timer system.
If I ask the Tado to heat the receiver clicks to turn central heating on but the boiler doesn’t respond.
Any help would be much appreciated
1
Comments
-
I think you may need to link out the timer on the front of the boiler0
-
Or possibly leave the old timer on constant so it isn’t timed or off0
-
Thank you for the reply if I leave the old timer constantly on the central heating system is constantly on0
-
It’s not wired correctly.
0 -
I have followed the combi boiler live linked0
-
So on the old timer you should see to black wires going in and then two wires coming out that goes into the timer . If you turn the power off . Disconnect the two wires going into the timer and put a link in . See if that works . Just means the old timer isn’t connected anymore0
-
I’ll give that a a go thank you0
-
All sorted turned out the receiver box was to close to the boiler which was interfering with the boiler1