Wiring to danfoss - honeywell
Hey there. i am a little confused how am i supposed to wire this, and also what configuration code choose later on. The system i have is Danfoss district heating, but i assume it works on Honeywell t3 wired thermostat, which only turns on/off Danfoss. When it does i can hear click noise. I am enclosing a pic of danfoss wiring.
there is also brown and green/yellow wire in the box. i believe brown is not plugged to anything.
Thanks!
Best Answer
-
@MiKMiK . This video Mounting and Installing a T3 Thermostat- European Model describes how your model of programmer is linked in. It confirms the suggestion given earlier.
It is important to check the voltage on ports A and B. Are they 24 volts or under, or at full mains voltage? Tado need this information.
If you are uncomfortable measuring voltage, a good idea would be to contact the firm which delivers your district system and ask them whether ports A and B are meant to run
- at mains voltage simply serving as a switch
- operate as a 'NOVOLT' on-off switch, or
- as a digital connection, supporting a well accepted digital control protocol- and if so, what protocol do they want supported?
The guide (the video link referred here) mentions the option of installing a wireless thermostat which then mates with the programmer. Do you have a wireless thermostat mated to that T3H110A, or is it just wired as is, nothing else?
Hope this makes sense.
0
Answers
-
Suggest you contact Tado and ask them about the T3H110A thermostat programmer. It seems that the cables migrate like this:
- Port A to Tado COM
- Port B to Tado NO.
But please contact Tado support and check.