Added VR33 to EcoTech Plus 937 and radiators heating all the time.
Best Answer
-
From my side, looking at the tado account shich shares your forum-email address, I see some weird values until Nov 17th just after midnight. Then no bus communication until Nov 18th in the afternoon, and then normal Opentherm communication since Nov 18th afternoon. So it seems you solved it.
For reference, I found this picture in my documentation of a customer who has a VR33 installed by the manufacturer (OT was/is mandatory in the Netherlands) in a Vaillant boiler. So I assume this is correct, but I'm not a VR33 expert.
0
Answers
-
Hi. Check this list and decide on the actions needed.
- Get in touch with Tado through the app and asked them for a specific set of instructions to make this work? If they havent responded, pester them and come back here as well.
- If they have already provided you with full instructions and you've complied, contact support again and ask them to assist with the final reconfiguration steps. If they dont respond, come here and we can try and escalate this.
- Is that radiator in the hallway unassigned to a room?
Unfortunately most of us dont have first hand experience with X yet.
@Rob is this your patch?
1 -
Thanks for coming back to me. I think I have just managed to get it working. Reseated the cables for the VR33 which got me diagnostic D.090 eBUS controller recognised. Boiler was still running continuously. Looking in the error log had F49 which comes up as eBUS short. Removed the wire jumper on the ebus connector on the main board - which every comment I had found online said was necessary. After that the eBUS started working properly and D.023 showed heating status as blocked. I think this means that the jumper on the 24V=RT connector pretends to be a thermostat calling for heat all the time hence the boiler running all the time and once eBUS connection is working properly it overrides this jumper. As I now have a boiler that is working on opentherm I'm about to hit order on an X system. Looking forward to more than one bridge!0
-
@Rob Thankyou for getting back to me. Yes I believe I have sorted it, and having proved it works I have ordered a load of tado X components to upgrade. The picture you included is a bit confusing though. I think the boiler is probably an earlier version of the 937 as it has both X31 (ebus extension?sockets on the VR33 used - one links to the X31 on the main PCB and the other links through to the Actostor storage module at the back of the boiler. However the opentherm connector on the VR33 has a loop cable in it. It looks like the ebus input at the right of the board is being used rather than opentherm.0
-
@Joseph95 - hope this
0 -
[url=https://ibb.co/1m6VkyN][img]https://i.ibb.co/NyShMDq/20241117-000905.jpg[/img][/url]
[url=https://imgbb.com/]upload photo[/url]0 -
[url=https://ibb.co/1m6VkyN][img]https://i.ibb.co/NyShMDq/20241117-000905.jpg[/img][/url]
[url=https://imgbb.com/]upload photo[/url]0 -
Hello Kissarmy… Is the boiler modulating or in Relay mode? Also are you able to control boiler temperature with Tado app? I installed VR33 today.. Wireless receiver indicates green light for OPENTHERM but seams to be working in relay mode… did you need to play with any boiler settings..Any feedback would be much appreciated..
0 -
The boiler was operating in modulating mode as far as I could tell. The display showed a low flame level. For relay I would have expected to see a much higher flame. I did not make any adjustments to the boiler. I used the Pro app to set the Tado system to opentherm protocol and checked the diagnostics menu on the boiler - think it was D:090 or maybe D:091 - on a train so not able to check sorry - to confirm that eBus communication was working. My system is currently back to using V3+ outputting eBus directly until I can work out a way of mounting the VR33 remotely.0
-